[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] problem of sky temperatures



Pauline,
  In addition to Adrien's response, the sky temperature model that is implemented in Type15 (when reading meteonorm files for example) is the same one that is in the TESS Type575.
Best,
 David


On 8/22/2012 08:22, ITF - Adrien JEZEQUEL wrote:
Hi Pauline,

This subject was ever treated in the past :
https://mailman.cae.wisc.edu/pipermail/trnsys-users/2009/004373.html

Different models exist to evaluate sky temperature.
That's why you may find differents values.
Meteonorm software use SoDa/ESRA clear sky model.

In trnsys, you may use  :
  • type69a : cloudiness factor is not controled by user
  • type69b : cloudiness factor is an input of the type
  • type575a and type575b (In TESS library only)

If you compare sky temperature given by meteonorm data and sky temperatures given with type69b with the same cloudiness factor as meteonorm data, results won't be so different.

Best regards


www.itf.biz
www.itf.biz
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
ITF
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel@itf.biz ou aj@itf.biz
Afin de contribuer au respect de l'environnement, merci de n'imprimer cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email
Le 22/08/2012 11:17, Pauline GELIN a écrit :

Hello,

 

For a project I would like to check if the effective sky temperature done by the weather type 9 (Meteonorm) is the same than the temperature calculated in the type 69 (with 4 inputs from the type 9).

In fact there are different.

How can we explain that whereas there is the same descriptions?

 

Thank you very much for your answers.

 

Best regards,

 

Pauline Gelin

 

 

Description :
                            cid:image007.jpg@01CC9EDB.F49EDC60

Description : Description :
                            Description : Description : Description :
                            logo Woopa

KATENE

 

10 avenue des Canuts – 69120 VAULX EN VELIN

0437453347

 

 



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley@tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com