William,
 I would be very careful in using the Type60 with an internal heat exchanger and low flow rates, particularly if you are anywhere close to laminar flow. I have run into some problems with its internal calculation of the heat exchanger UA as well. If possible, I would recommend that you use Type534 from the TESS Storage Libary. In my experience, the UA calculation for that tank model's internal heat exchanger is more robust.
Best,
 David


On 11/10/2011 04:32, William.Logie@solarenergy.ch wrote:

Dear TRNSYS folk,

 

I was wondering if anyone can shed some light on Type60, in particular low flow operation of the immersed heat exchanger model (IHX). I’m using the 16.01.0003 edition of TRNSYS and 2005-01-31 – Mku version of Type60.

 

I’ve been happily simulating high-flows (>40kg/hr per m^2 collector area) but run into non-convergence warnings (and infinite loops) with, for example, a specific collector flow of 10kg/hr; storage volume 400 litres with 25 nodes and a simulation time step between 3 and 6 mins; http://sel.me.wisc.edu/trnsys/mailinglist/archive2004/msg00640.html. I have tried reducing the flow rate to a minute and even less but non-convergence persists (for an annual simulation that doesn’t abort I get between 2 and 5 thousand warnings). Some exemplary energy balances (measured with Type60) are as follows;

 

10kg/hr:

Q_coll + Q_aux = 13934081.86 kJ

Q_losses + Q_dhw = 13920759.15 kJ

Q_coll + Q_aux – Q_losses – Q_dhw = Q_err = 13322.71 kJ

 

50kg/hr:

Q_coll + Q_aux = 13961476.57 kJ

Q_losses + Q_dhw = 13947209.16 kJ

Q_coll + Q_aux – Q_losses – Q_dhw = Q_err = 14267.41 kJ

 

Is this all within reason? If not, any tips?

 

Kind regards,


William Logie
Forschung / Research

Institut für Solartechnik SPF: Adresse / Website
Hochschule für Technik Rapperswil HSR
Tel. +41 55 222 48 34
Fax +41 55 222 48 44


 



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************