Welcome to the TRNSYS Users Forum.

The forum is a place where people can interact and have discussions about different topics involving the use of the TRNSYS software package. Here you can post topics for discussion or questions on using TRNSYS and get advice from other users or TRNSYS experts. This forum is not intended for detailed technical support. Users should contact their distributor’s hotline for such assistance.

Some tips for success on using the forum:

  • Follow the Forum Rules posted in Forum Administration.
  • There are categories for different types of topics and questions. Post your topic or question into the proper category.
  • Before posting a topic or question search the existing topics  (and the TRNSYS Users listserv archive or Post archive) to see if a similar topic or question has already been answered.
  • Use a descriptive topic name. Don’t use attention getting subjects, they don’t get attention and only annoy people.
  • State the version of TRNSYS and which add-ons your are using.
  • Include enough specific details for your topic of question to be answered. Just posting “Why am I getting an error?” without describing the specific error and what you are trying to do when you get the error will not receive a response that fixes your issue.
  • Remember when people help you, they are doing you a favor. Be patient, help people out by posting good descriptions of what you need help with, and be polite even if a response does not solve your issue.
  • Moderators may edit your post for clarity or move your topic to a more appropriate category.

Notifications
Clear all

Type 941 (air-to-water heat pump) - problem with exiting fluid temperature control

1 Posts
2 Users
0 Reactions
36 Views
0
Topic starter

Dear All,

I am a novice TRNSYS user and I am modelling a system with an air-to-water heat pump (type 941) with a buffer tank (type 534) and a heat receiver in the form of a low-temperature radiator (type 1231). The system would operate over a temperature range of -10°C to 15°C.

I would like to use weather control, whereby the temperature of the fluid exiting the heat pump would increase as the outside temperature decreases. Regardless of the control I use, I cannot achieve the desired effect and the opposite happens - the temperature at the exit of the heat pump keeps rising as the outside temperature increases.
 
I would be grateful for any help.
This topic was modified 3 months ago by AOtrnsyspl
1 Answer
0

@aotrnsyspl

Type941 models an on/off heat pump whose compressor can only run at one speed. In order to vary the outlet fluid temperature, a heat pump needs to have a variable speed compressor. There are models of variable speed compressor heat pumps available in the updated (v18) TESS HVAC library.

kind regards,

 David

 