Welcome to the TRNSYS Users Forum.

The forum is a place where people can interact and have discussions about different topics involving the use of the TRNSYS software package. Here you can post topics for discussion or questions on using TRNSYS and get advice from other users or TRNSYS experts. This forum is not intended for detailed technical support. Users should contact their distributor’s hotline for such assistance.

Some tips for success on using the forum:

  • Follow the Forum Rules posted in Forum Administration.
  • There are categories for different types of topics and questions. Post your topic or question into the proper category.
  • Before posting a topic or question search the existing topics  (and the TRNSYS Users listserv archive or Post archive) to see if a similar topic or question has already been answered.
  • Use a descriptive topic name. Don’t use attention getting subjects, they don’t get attention and only annoy people.
  • State the version of TRNSYS and which add-ons your are using.
  • Include enough specific details for your topic of question to be answered. Just posting “Why am I getting an error?” without describing the specific error and what you are trying to do when you get the error will not receive a response that fixes your issue.
  • Remember when people help you, they are doing you a favor. Be patient, help people out by posting good descriptions of what you need help with, and be polite even if a response does not solve your issue.
  • Moderators may edit your post for clarity or move your topic to a more appropriate category.

Notifications
Clear all

Sequencing heat pump activation

1 Posts
2 Users
0 Reactions
9 Views
0
Topic starter

Hi,

I want to model a system which activates heat pumps (Type 793) sequentially in case the temperature of different zones drops below a certain amount and the need for heat exceeds the amount that a single heat pump can provide. How can I do it?

Thanks

Shams

1 Answer
0

@shamsoddinghiami Do you want to control the sequential activation off of a zone temperature, or off of the total desired load?

If you want multiple on/off signals from a monitored temperature (signal device 1 ON when the temperature drops below 20 C, device 2 ON when the temperature drops below 19 C, etc.), you can use any of the multi-stage differential controllers in the TESS Controllers library. Types 1502/1503 allow up to 100 sequential stages with different setpoints for each stage. The user can define whether prior stages should stay on or turn off when a new stage comes on. Types 970/971 are similar to Types 1502/1503, but allow the user to specify individual deadbands for each stage, as well as minimum run-time or time delays before starting/stopping each new stage. If you're monitoring multiple zone temperatures, you may need an equation block to calculate the minimum/maximum temperature of all zones first, then send that value to the controller. 

If you want to control a central plant of devices based on the total desired load, you can use the staged device controller (Type 910) in the TESS Controllers library. The staged device controller is given a total desired value (total load to supply) as an input at each time step. It will run device 1 until its part-load ratio exceeds a user-specified threshold, then add a second device and share the load equally between the two until both device's maximum part-load ratio is exceeded and a third is brought online, and so forth. 