Amirreza, I would try three things. One is to set the mass flow rate and inlet temperature to the
active layer as INPUTS to Type56 (they may already be set that
way) and then run some cases where you use a forcing function or
an equation to switch between a high inlet temperature and a low
inlet temperature and between flow on and flow off. If the flow
rate and inlet temperature are constant then sometimes it can be
hard to see what their effect is because everything is steady
state. In doing this, make sure that your weather conditions are
cold; if the building's ambient condition is close to 26C then
putting 26C water into the active layer is not going to have much
of a visible effect The second thing I would recommend is to put a layer of
insulation on the side of the concrete that you are NOT trying to
condition with the active layer. We ran into this same situation
where there was a mezzanine that had a radiant floor. It was
impossible to control the temperature of the mezzanine area
without insulating the underside of that floor (which was also the
exposed ceiling below). It may be that a lot of your energy is
going up instead of down. Lastly, instead of watching the air temperature, look at the surface temperature of the concrete. It should be quite close to the temperature of the active layer. That surface temperature should be more directly impacted by the active layer than the air temperature is best, David
On 1/6/2023 3:56 PM, Amirreza Heidari