Dear Adnan, you may use Type 14 got the time depending set temperature as an output which you may use for further control. Keep in mind that controls by equation may cause instability. It is recommended to use a controller Type with temperature bands (e.g. Type 2) Marion Marion Hiller +49 711 679 76 32 |
hiller@transsolar.com Transsolar SoftwareEngineering Stuttgart | Munich | Paris | New York Transsolar Energietechnik GmbH | Curiestrasse 2 | 70563 Stuttgart | Germany CEO: Matthias Schuler, Thomas Auer, Stefan Holst, Dieter Schnelle
Registered at Amtsgericht Stuttgart HRB 23347 | USt-IdNr.: DE 152272639 Von: TRNSYS-users <trnsys-users-bounces@lists.onebuilding.org>
Im Auftrag von adnan rasheed via TRNSYS-users Dear Marion Hiller , i checked Type 14 output will not work in this situation. Actually i want to control natural ventilation window open and close according to the set point, at the corresponding time span. As i write before temperature is room temperature, on behalf of that window should be open and close. if room
temperature is high than the set value at particular time span window should open (natural ventilation). 00 to 5h.... temp set point 18 C 5-10h.... temperature set point 22 C 10-18h....23 C 18 -24h...24 C Thanks On Thu, Mar 26, 2020 at 4:58 PM Marion Hiller via TRNSYS-users <trnsys-users@lists.onebuilding.org> wrote:
-- Adnan Rasheed Post-doc Research Fellow Kyungpook National University Daegu, South Korea. +82-102762-0105 |