Hello Jeff,
First, thanks for
the answer.
I isolated the heat pump into a new project, created 2
equation components representing source and load side flow
and inlet temperatures but the heat pump is still having
quite strange COP results, and I have no idea why.
Here is basically what I did:
Timestep: 0.1h
Type 927 (parameters 15 to 18):
rated heating capacity 177kW
rated power: 46kW
rated load/souce flowrate: 9.5 l/s
I attached my expected performance curve according to the
performance data from TESS library for type 927, and the
results from some of the tests I performed.
The main thing that I don't understand is why, even on the
test project, there are so many scenarios that is in direct
conflict with the performance data sheet.
By reducing the load-side flowrate and
increasing the EWT for the load-side, the heating COP went
to above 5, when according to the performance curve, both
scenarios should decrease COP.
By having load-side EWT of 20 degrees C and flowrate equal
to the rated value (9.5 l/s), the COP was near 3. By
decreasing only the flowrate, COP increased to almost 4
(again, against performance curve).
And last, by decreasing source-side EWT, COP increased as
well, when it should decrease.
Am I misunderstanding the system? Or I made a mistake even
on the test project, as well?
On my main project I have a storage tank added and there are
no errors during the simulation. I think my only problem is
understanding this COP curve.
Thank you again,
Vitor L.