The outlet air temperature of the building is the air node temperature. Type56 does not have outputs for the mass flow rate of air out of a space because it assumes that all of the air that goes into a zone through one of the VENTILATION types also leaves that zone by the same mechanism. Thus you can take the Type697 output flow rate as the input flow rate to the fan that is moving air between the cooling coil and the zone. Please note that if you are using CONTAM (Type97/Type98) or TRNFlow the assumption that VENTILATION air supply and return is balanced no longer necessarily true. kind regards, David