Dear Kaouther,

 

we have good experience using the Nostandard Type 399. Here is a documentation of the type: http://trnsys.de/download/de/ts_type_399_en.pdf

And an order sheet if you are interested: http://trnsys.de/download/en/TS_Nostandard_Ordersheet_en.pdf

 

Best
Jakob

 

 

__________________________________________________________________________________________________

 

Jakob Merk M.Sc.

 

Transsolar Energietechnik GmbH

Curiestraße 2

70563 Stuttgart

http://www.transsolar.com

Transsolar: KlimaEngineering- Technologien für energieeffizientes Bauen und Nutzerkomfort in Gebäuden

Stuttgart – München – New York – Paris

Geschäftsführer :Diplom-Ingenieur Matthias Schuler, Diplom-Ingenieur Thomas Auer, Diplom-Physiker Stefan Holst, Diplom-Betriebswirt Dieter Schnelle

Eingetragen beim Amtsgericht Stuttgart HRB 23347,

Steuernummer: 99073/00911,USt-IdNr.: DE 152272639

 

 

 

Von: TRNSYS-users [mailto:trnsys-users-bounces@lists.onebuilding.org] Im Auftrag von via TRNSYS-users
Gesendet: 04 May 2017 16:06
An: Jeff Thornton <thornton@tess-inc.com>; TRNSYS users mailing list at OneBuilding.org <trnsys-users@lists.onebuilding.org>
Betreff: [TRNSYS-users] type for simulating MCP materials

 

Dear Jeff Thornton

I would like to ask you if there is a type in TRNSYS wich simulate an MCP (material phase change) model

thank you

 

Kaouther Ben Nasr
Docteur Ingénieur\\Génie Énergétique
Maître assistant à l'ENAU
Chercheur au CRTEn\\Technopôle Borj Cédria
mobile: +216 53 48 44 38

 


De: "Jeff Thornton via TRNSYS-users" <trnsys-users@lists.onebuilding.org>
À: "Amirreza Heidary" <amirrezaheidarysbu@gmail.com>, "TRNSYS users mailing list at OneBuilding.org" <trnsys-users@lists.onebuilding.org>
Envoyé: Samedi 29 Avril 2017 16:52:42
Objet: Re: [TRNSYS-users] problem with differential controller

 

Amirreza,

 

Real solar collectors do the same thing under certain circumstances.  From a first glance I would say your dead bands are too tight - typically we see 10/2 not 5/2.  It's also possible that your collector pump flow rate is  too high.  With collectors connected in series you typically have a pump flow rate the same as if you had only one collector.  Collectors are designed for a given maximum flow rate for pressure drop reasons.  For example, assume we had a collector that wanted 450 kg/h of flow and we had 6 in series.  We would run the pump at 450 (each collector gets the 450 that way).  You wouldn't run your pump at 2700 (450 x 6) or the pressure drop would be ridiculously high.  If you have that high of a flow rate you'll get exactly what you are seeing in your project.  With no flow the collector temperature is above the deadband but when the pump turns on the high flow rate causes the outlet temperature to drop below the lower deadband.  The controller can't find a solution since both are correct and will oscillate between on and off.

 

Jeff

TESS Inc

 

Sent from my iPhone


On Apr 29, 2017, at 2:36 AM, Amirreza Heidary via TRNSYS-users <trnsys-users@lists.onebuilding.org> wrote:

 

Dear All

I'm using a 5 collectors in series with a differential controller to turn on the pump when the difference of collector outlet and inlet temperatures is more than 5 and turn it off when it is less than 2.But the signal and collector output temperatures are fluctuating too much, also the signal is not compatible with temperature variations.as you can see in the following diagram, the signal is 1 when the outlet temperature is at maximum ! 

(red line is collector outlet temperature and orange line is the controller signal)

Inline image 1

Inline image 2 

 

--------------------------------------------------------------------------------------------------------------------------------------------------

amirrezaheidary

master student of energy systems Engineering

Sharif university of technology

Tehran-Iran

E-mail address:

heidari@energy.sharif.edu

amirrezaheidarysbu@gmail.com

P Save a tree... Please don't print this E-mail unless you really need to.                                                                                                                              

 









  Sent with Mailtrack

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org


_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org