Nipaporn, If you want a heating controller (ie a controller that turns equipment on when the room temperature falls below 26.5C and allows it to stay on until room temperature reaches 27.5C) then set the first input to the middle of your set point temperature range (27C). The second input will be the temperature that you are monitoring (the room temperature). The fifth input (upper dead band) would be set to 0.5C and the sixth input (lower dead band) would be set to -0.5C. If you want a cooling controller (ie a controller that turns equipment on when the room temperature rises above 27.5C and allows it to stay on until room temperature falls to 26.5C) then set the second input to the middle of your set point temperature range (27C). The first input will be the temperature that you are monitoring (the room temperature). The fifth input (upper dead band) would be set to 0.5C and the sixth input (lower dead band) would be set to -0.5C. Kind regards, David On 5/14/2013 23:22, Nipaporn Nutprasert
wrote:
-- *************************** David BRADLEY Principal Thermal Energy Systems Specialists, LLC 22 North Carroll Street - suite 370 Madison, WI 53703 USA P:+1.608.274.2577 F:+1.608.278.1475 d.bradley@tess-inc.com http://www.tess-inc.com http://www.trnsys.com |