Hi Jeff,
Thanks a lot for your insightful comments to the queries raised ! I followed your lead and found the cause of the problem. The root cause actually came from an erroneous data input in the part load file being fed to the chiller.
As a result, when I increased the ECWT and consequently decreasing the capacity of the chiller, the chiller was running at a higher part load and hence steering
away from the erroneous part load data that gave the unexpected spikes. When the part load data was corrected, the chiller is behaving as expected.
Now all the phenomenon observed can be explained ! Once again, I would like to thank you for pointing me to the correct direction of investigation.
And thanks to everyone who had spent their time to think through the queries raised.
Best Regards,
From: Jeff Thornton [mailto:thornton@tess-inc.com]
I would run a simulation with just the chiller in it and vary one factor at a time to make sure the chiller is behaving as expected. If I was a betting man, I would say that the part load impacts are what are driving your COP swings. As the ECWT decreases,
the capacity of the machine increases and for a given load, the part-load ratio decreases. If you have a rather part-load curve on the chiller it would explain what you are seeing. Jeff --- Jeff Thornton President - TESS LLC 22 N. Carroll Street, Madison WI USA 53703 Office: (608) 274-2577 Fax: (608) 278-1475 E-Mail: thornton@tess-inc.com On 03/27/2013 2:29 am, #YEO KEAT KEE# wrote:
|