[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] User-defined CHTC: pane temperature calculation diverging



Hi Marion,

That was a very interesting suggestion, thank you. I am using type93 for the input value recall, and placing it in front of type56 did indeed stop the convergence problem.

Kind regards,

Sarah

ir. arch. Sarah Leenknegt - KU Leuven - Building Physics Section - Department of Civil Engineering - Kasteelpark Arenberg 40, bus 2447 - B-3001 Heverlee, Belgium - tel. +32(0)16321347

Op 2/26/2013 8:40 AM, Marion Hiller schreef:
Sarah,

in general, very low CHTC values cause convergence errors in all
simulation programs. Therefore, the min. values is often fixed to value
of 1W/m² = 3.6 kJ/h.
If the min. value is very low and the initial surface temperatures are
set equal to the initial zone temperature convergence problems like pane
temperature diverging may occur.

I'm not sure but do you use Type93 for input recall or not?

In addition, I have in mind that the component order could help with
convergence problems. You may check both orders  Type93 before and
after Type 56.

Marion



Dipl.-Ing. Marion Hiller
TRANSSOLAR: KlimaEngineering - Technologien für energieeffizientes Bauen
und Nutzerkomfort in Gebäude
Munich - New York - Stuttgart + 49.711.67976.0

Transsolar Energietechnik GmbH, Curiestrasse 2, 70563 Stuttgart
Amtsgericht Stuttgart - HRB 23347, Steuernummer 99073/00911, USt-IdNr.:
DE152272639
Geschäftsführer: Dipl.Ing. Matthias Schuler, Dipl.Ing. Thomas Auer,
Dipl.Phys. Stefan Holst, Prof. Dipl.-Ing. Bleicher

-----Ursprüngliche Nachricht-----
Von: Sarah Leenknegt [mailto:sarah.leenknegt@bwk.kuleuven.be]
Gesendet: Montag, 25. Februar 2013 19:03
An: David BRADLEY
Cc: trnsys-users@cae.wisc.edu
Betreff: Re: [TRNSYS-users] User-defined CHTC: pane temperature
calculation diverging

Dear David,

Thank you for your answer. I know about Type93, in fact I have tried
with one or four time steps, did not make a difference. About the
correlation, I have manually tried several variable or constant values,
which I would expect would challenge convergence, but as long as I did
not use the input value recall, the simulation would run.
In the meantime, I was experimenting a bit, and found the following
strange solution. The first equation does work, the second one doesn't..
(1) max(0.01,2*abs(surftemp-airtemp)**0.31 + 0*time)
(2) max(0.01,2*abs(surftemp-airtemp)**0.31)

I can accept this as a workaround, but would like to understand why it
is needed..

Thanks,

Sarah

ir. arch. Sarah Leenknegt - KU Leuven - Building Physics Section -
Department of Civil Engineering - Kasteelpark Arenberg 40, bus 2447 -
B-3001 Heverlee, Belgium - tel. +32(0)16321347

Op 2/25/2013 6:49 PM, David BRADLEY schreef:
Sarah,
   If you are using Type93 for the input value recall please be aware
that its first output is not delayed; it is the value of the input at
the current iteration. You need to use the second output in order to
get the input from the last time step.

   Whether or not the above fixes the problem, I don't think that
Trnsys3D has anything to do with the issue. Trnsys3D is really just a
way of getting data into TRNBuild in a more visual manner. You might
also look at your convection coefficient correlation. The correlations
that are built in to Type56 raise the surface to air temperature
difference to a power less than 1 (dampening the effect of the
temperature difference). It may be that your correlation is too
sensitive to the temperature difference, leading to convergence
problems.
Kind regards,
  David


On 2/25/2013 04:49, Sarah Leenknegt wrote:
Dear TRNSYS-user,

I have the following problem. I am trying to input a CHTC-correlation
in the building model. I am using the input value recall to get the
surface and air temperature of one timestep before. I can calculate
the CHTC and plot it with an online plotter, but whenever I try to
use it as an input, a get the "pane temperature calculation is
diverging" warnings from the start of the simulation and the
simulation stops. The CHTC is non-zero and positive, and for now, the
equation used is simply max(1,2*abs(surftemp-airtemp)). If I
calculate a variable CHTC without using the surface and air
temperature, the simulation runs without error.

I have used TRNSYS3D to make my one-zone model, including one window
facing south-west (TURN = -45°) and 4 air nodes. I am using the
detailed radiation model, so all air nodes are combined into one
zone. Viewfactors and insolation matrix are generated without
problem. I have gone back to the most basic simulation, using only
the idf imported in a 3D building project standard template, with a
standard Meteonorm Uccle climate.

Following recommendations in previous posts, I have set the CHTC at
the window to the standard fixed values for inside and outside. I
have also checked if something went wrong when drawing the window in
sketch-up, but I do not see any lines that shouldn't be there.
Changing to a different glazing doesn't help either.

Can anyone give me some help as to what else I can try? I have done
this before without problems, but it is the first time I try it with
trnsys3D.
Please answer to me privately as well, as I am not subscribed to the
mailing list.

Kind regards,

Sarah

--
ir. - arch. Sarah Leenknegt,
Afdeling Bouwfysica, Dept. Burgerlijke Bouwkunde,
Faculteit Ingenieurswetenschappen, KULeuven,
Kasteelpark Arenberg 40 - bus 2447, 3001 Heverlee, België

sarah.leenknegt@bwk.kuleuven.be
tel. 016 321347
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users