Rakesh,
  It looks as though you are passing some incorrect variables back to the building model and that the variables you are passing (T_HEATING, T_COOLING, and RH_COOLING) are defined in the building but aren't actually implemented in your zone. The inputs that you need to pass from the furnace model to the building model are the furnace's outlet air temperature, RH, and flow rate. You will need to open TRNBuild and define a VENTILATION type in your zone. A couple hints:

1. Specify that you are going to provide air flow rate as a mass flow and change the flow rate from a constant value (the default) to an input.  Give the input a name like MVNT_55FC41
2. Specify that you are going to provide the temperature of the ventilation air as an input. Give the input a name like TVNT_55FC41.
3. Specify that you are going to provide the humidity of the ventilation air as an input and as an RH (which is the default). Give the input a name like RHVNT_55FC41.

When Type56 talks about ventilation, it means a stream of air, not necessarily the zone's fresh or outdoor air as is sometimes traditional in the US.
best,
 David


On 7/26/2011 15:08, Rakesh Kaushik wrote:
Dear trnsys user,

I created a type-56 3D model for a zone, and I introduced the type 108 thermostat to monitor the temperature in the zone with the help of fan, furnace and auxiliary cooling unit, and I need little help to figure what I am doing wrong I attached my model with this email.

Thank you very much in advance  

Regards,
Rakesh Kaushik
Graduate Student
Department of Mechanical Engineering
University of Dayton
Cell: 937-239-5924

_______________________________________________ TRNSYS-users mailing list TRNSYS-users@cae.wisc.edu https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley@tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com