Re: [TRNSYS-users] type 16



Dear Mr. Jeff,

      Many thanks for your patient reply!

      I used Type 16a, but there is an ERROR as follows:

*** Fatal Error at time   :         7.618000
    Generated by Unit     :    16
    Generated by Type     :    16
    Message               : An simulation timestep is greater than the data timestep for the radiation calculation.  The simulation timestep needs to be reduced.
 
 
*** Notice at time        :         7.618000
    Generated by Unit     :     2
    Generated by Type     :    56
    Message               : Geometrical distribution factors for direct solar (GEOSURF) in zone   1 did not always sum up to unity.  normalized values were used for these timesteps!
 
 
*** Notice at time        :         7.618000
    Generated by Unit     :     2
    Generated by Type     :    56
    Message               : Geometrical distribution factors for direct solar (GEOSURF) in zone   2 did not always sum up to unity.  normalized values were used for these timesteps!
 
 
*** Notice at time        :         7.618000
    Generated by Unit     :     2
    Generated by Type     :    56
    Message               : Geometrical distribution factors for direct solar (GEOSURF) in zone   3 did not always sum up to unity.  normalized values were used for these timesteps!


        And I reduced the time step, after that this ERROR is still appearing.

       Please give me some advices about that!


       Thanks a lot!

       Br.

wang


2011/6/14 王洋 <wanghongyang1767@gmail.com>
 
2011/6/14 Jeff Thornton <thornton@tess-inc.com>
Steps to resolve your simulation problem:

1) Read the documentation for Type 9 and Type 16 carefully.  Pay special attention to the section on interpolating data in Type 9 (don't with radiation) and the section in Type 16 about solar time versus local time.  Consider daylight savings time (if applicable).

2) Create your external data file with the weather data.

3) Find the Type 9 data reader and choose the expert mode (Type9e).  Choose the settings that match how your data file is set up. 

4) Drag out a Type 65 online plotter and make sure that the simulation is reproducing the data from the external file correctly.

5) Then find the radiation processor and choose the mode where only the total horizontal radiation is know (Type16a).  Choose the parameters carefully.

6) Connect the total horizontal radiation from the data reader to the radiation processor.  Also connect the time of last read and time of next read inputs,

Repeat step 4.

Jeff

Jeff Thornton
President - TESS, LLC

22 North Carroll Street - Suite 370
Madison WI 53703 USA

Phone: 608-274-2577
Fax: 608-278-1475
E-mail: thornton@tess-inc.com
Web: www.tess-inc.com



----- Original Message -----
From: "王洋" <wanghongyang1767@gmail.com>
Sent: Tue, June 14, 2011 8:13
Subject: [TRNSYS-users] type 16

Dear Mr. Jezequel,

  Many thanks for your answer.

 Yes, I saw the Example: RadiationProcessing etc.It uses Type 16i i.e. Total horiz. Diffuse known(Mode 5).  But I only get the Global Radiation data, I can't get the Diffuse radiation on horizontal from our weather station.

Besides that, it uses Type 9f which links to Type 16i. I can't find Type 9f in Proforma in Simulation Studio.



Thanks a lot!

Br.

wang

2011/6/14 <trnsys-users-request@cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
       trnsys-users@cae.wisc.edu

To subscribe or unsubscribe via the World Wide Web, visit
       https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
       trnsys-users-request@cae.wisc.edu

You can reach the person managing the list at
       trnsys-users-owner@cae.wisc.edu

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."

Today's Topics:

  1. Output Time Base for Massive Construction (Rebecca Ward)
  2. Type 56 Active Layer Not Saving (Devin Rohan)
  3. type 16 (??)
  4. Re: type 16 (Adrien JEZEQUEL - ITF)


---------- 已转发邮件 ----------
From: "Rebecca Ward" <rmw61@cam.ac.uk>
To: <trnsys-users@cae.wisc.edu>
Date: Mon, 13 Jun 2011 19:16:18 +0100
Subject: [TRNSYS-users] Output Time Base for Massive Construction

Hi,

I’m new to TRNSYS and am modelling a brick building with very thick walls in places but which has an extension with fairly lightweight thin walls.  In order to pass the stability criteria, I found it necessary to increase the output time base to 2 – what I’m wondering is how this affects the rest of the analysis, in particular the thinner lightweight walls?

Thanks for any help you can give.

Regards,

Rebecca



---------- 已转发邮件 ----------
From: Devin Rohan <drohan@purdue.edu>
To: trnsys-users@cae.wisc.edu
Date: Mon, 13 Jun 2011 17:04:56 -0400
Subject: [TRNSYS-users] Type 56 Active Layer Not Saving
1.) When I'm defining an active layer, the save button is not accessible.  So I put it into my wall type and I can save the wall type with the active layer in it.  When I close out of TRNBuild and start a new project, the layer I defined as an "active layer" get assigned to a "massless layer" and the active layer option is not available.  Any help as to why this happens is appreciated.
 
--
Devin M. Rohan, LEED Green Associate
Purdue University
Civil/Architectural Engineering
drohan@purdue.edu


---------- 已转发邮件 ----------
From: 王洋 <wanghongyang1767@gmail.com>
To: trnsys-users@cae.wisc.edu
Date: Tue, 14 Jun 2011 11:22:41 +0200
Subject: [TRNSYS-users] type 16
Dear all,

        I added our institute own weather data into TRNSYS using Type 9. But I also want to add the other weather data: Global Radiation into TRNSYS. As I knew, I need Type 16 and Type 9. But I don't know detailed setting and defination of Type 16. Please give me some advices in details.
        E.g. 1. Which Mode should I select? Mode 2? Because there are Global radiation, Outdoor temperature and Humidity and wind speed, wind direction and Air pressure in our weather station.
        2. In details which Inputs and Outputs of Type 16 need I link to Type 9 and others?
        3. How to set and define the Parameter, Input and Output in details?

        Many thanks!
 
       Br.

     wang

2011/6/13 <trnsys-users-request@cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
       trnsys-users@cae.wisc.edu

To subscribe or unsubscribe via the World Wide Web, visit
       https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
       trnsys-users-request@cae.wisc.edu

You can reach the person managing the list at
       trnsys-users-owner@cae.wisc.edu

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."

Today's Topics:

  1. Question(solar radiation) (=?EUC-KR?B?udrB2L/4?=)
  2. TRNSYS Active Layer Flowrate (Devin Rohan)
  3. type 700 efficiencies (Pablo D?az N??ez)


---------- 已转发邮件 ----------
From: 박준원<flowrime@naver.com>
To: <trnsys-users@cae.wisc.edu>
Date: Mon, 13 Jun 2011 20:33:02 +0900
Subject: [TRNSYS-users] Question(solar radiation)

Hi!!

I am a Korean student, i'm having some trouble with solar radiation.

 

I want to get "Indoor solar radiation" using Type56b(Multi zone)...

 

But. I dont know output value about solar radiation..

 

I think,  Ntype 73 (zone output) is zone solar radiation, is it right??

 

However i dont know unit of that..

 

So.. My question are..

 

1. is Ntype 73 zone solar radiation? so what's the unit??

 

2. if not Ntype 73, How can i get the indoor solar radiation?

 

 

thanks to all,



---------- 已转发邮件 ----------
From: Devin Rohan <dmrohan@gmail.com>
To: trnsys-users@cae.wisc.edu
Date: Sat, 11 Jun 2011 20:10:01 -0400
Subject: [TRNSYS-users] TRNSYS Active Layer Flowrate
The Type 56 manual suggests that the specific mass flow rate be greater than 13 kg/h-m^2.  Say I wanted to convert this to mass flow rate in kg/s and the fluid was flowing through a 3/8" (or 9.525 mm) inside diameter pipe.  Here's what I'm doing...
 
A_pipe= (pi*D^2)/4 = (pi*.009525^2)/4= 7.1256 E-5 m^2
 
13 kg/h-m^2   x   (7.1256 E-5 m^2)   x   (h / 3600 sec)  =  2.573 E-7 kg/s
 
This seems like an awfully low mass flow rate, since what I've seen in literature for floor heating applications is around .05 kg/s.  Am I missing something here?

--
Devin M. Rohan
drohan@purdue.edu


---------- 已转发邮件 ----------
From: "Pablo Díaz Núñez" <p.diazn87@gmail.com>
To: trnsys-users@cae.wisc.edu
Date: Mon, 13 Jun 2011 18:16:34 +0200
Subject: [TRNSYS-users] type 700 efficiencies
Dear trnsys users,
 
I am simulating and studying the behaviour of a central heating system of a residential building with gas boilers. For the boiler I'm using type 700, where combustion and boiler efficiencies are inputs. I need these values as a function of the intlet water temperature and the part load ratio for the model to work and I don't find this data in any boiler catalog. Only partial data like the boiler efficiency at rated power.
 
If somebody had any cataloge with this data I would be very thankful. Or maybe somebody knows any manufacturer who could provide me.
 
I know it's not a doubt or question about trnsys itself, but I'm a bit desperate.
 
Thanks in advance!

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users




---------- 已转发邮件 ----------
From: Adrien JEZEQUEL - ITF <a.jezequel@itf.biz>
To: trnsys-users@cae.wisc.edu
Date: Tue, 14 Jun 2011 12:42:47 +0200
Subject: Re: [TRNSYS-users] type 16
Dear Wang,

I think TRNSYS examples deal with weather data.
I suggest you to check examples in your local TRNSYS directory to see how to do.

Best regards

www.itf.biz
www.itf.biz
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
ITF 62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel@itf.biz ou aj@itf.biz
Afin de contribuer au respect de l'environnement, merci de n'imprimer cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email

Le 14/06/2011 11:22, 王洋 a écrit :
Dear all,

        I added our institute own weather data into TRNSYS using Type 9. But I also want to add the other weather data: Global Radiation into TRNSYS. As I knew, I need Type 16 and Type 9. But I don't know detailed setting and defination of Type 16. Please give me some advices in details.
        E.g. 1. Which Mode should I select? Mode 2? Because there are Global radiation, Outdoor temperature and Humidity and wind speed, wind direction and Air pressure in our weather station .
        2. In details which Inputs and Outputs of Type 16 need I link to Type 9 and others?
        3. How to set and define the Parameter, Input and Output in details?

        Many thanks!
 
       Br.

     wang

2011/6/13 <trnsys-users-request@cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
       trnsys-users@cae.wisc.edu

To subscribe or unsubscribe via the World Wide Web, visit
       https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
       trnsys-users-request@cae.wisc.edu

You can reach the person managing the list at
       trnsys-users-owner@cae.wisc.edu

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."

Today's Topics:

  1. Question(solar radiation) (=?EUC-KR?B?udrB2L/4?=)
  2. TRNSYS Active Layer Flowrate (Devin Rohan)
  3. type 700 efficiencies (Pablo D?az N??ez)


---------- 已转发邮件 ----------
From: 박준원<flowrime@naver.com>
To: <trnsys-users@cae.wisc.edu>
Date: Mon, 13 Jun 2011 20:33:02 +0900
Subject: [TRNSYS-users] Question(solar radiation)

Hi!!

I am a Korean student, i'm having some trouble with solar radiation.

 

I want to get "Indoor solar radiation" using Type56b(Multi zone)...

 

But. I dont know output value about solar radiation..

 

I think,  Ntype 73 (zone output) is zone solar radiation, is it right??

 

However i dont know unit of that..

 

So.. My question are..

 

1. is Ntype 73 zone solar radiation? so what's the unit??

 

2. if not Ntype 73, How can i get the indoor solar radiation?

 

 

thanks to all,



---------- 已转发邮件 ----------
From: Devin Rohan <dmrohan@gmail.com>
To: trnsys-users@cae.wisc.edu
Date: Sat, 11 Jun 2011 20:10:01 -0400
Subject: [TRNSYS-users] TRNSYS Active Layer Flowrate
The Type 56 manual suggests that the specific mass flow rate be greater than 13 kg/h-m^2.  Say I wanted to convert this to mass flow rate in kg/s and the fluid was flowing through a 3/8" (or 9.525 mm) inside diameter pipe.  Here's what I'm doing...
 
A_pipe= (pi*D^2)/4 = (pi*.009525^2)/4= 7.1256 E-5 m^2
 
13 kg/h-m^2   x   (7.1256 E-5 m^2)   x   (h / 3600 sec)  =  2.573 E-7 kg/s
 
This seems like an awfully low mass flow rate, since what I've seen in literature for floor heating applications is around .05 kg/s.  Am I missing something here?

--
Devin M. Rohan
drohan@purdue.edu


---------- 已转发邮件 ----------
From: "Pablo Díaz Núñez" <p.diazn87@gmail.com>
To: trnsys-users@cae.wisc.edu
Date: Mon, 13 Jun 2011 18:16:34 +0200
Subject: [TRNSYS-users] type 700 efficiencies
Dear trnsys users,
 
I am simulating and studying the behaviour of a central heating system of a residential building with gas boilers. For the boiler I'm using type 700, where combustion and boiler efficiencies are inputs. I need these values as a function of the intlet water temperature and the part load ratio for the model to work and I don't find this data in any boiler catalog. Only partial data like the boiler efficiency at rated power.
 
If somebody had any cataloge with this data I would be very thankful. Or maybe somebody knows any manufacturer who could provide me.
 
I know it's not a doubt or question about trnsys itself, but I'm a bit desperate.
 
Thanks in advance!

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users


_______________________________________________ TRNSYS-users mailing list TRNSYS-users@cae.wisc.edu https://mailman.cae.wisc.edu/listinfo/trnsys-users

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users