Rambod, I assume that by umin and umax, you mean inputs 4 and 5. If that is the case then this inputs simply define the range of the controller's output. If you want to control a pump between fully off and fully on at its rated flow rate then you might choose 0 and 1 for your limits (as in the SDHW-Feedback example). If you wanted the controller to set the flow rate directly then you would set umin to 0 and umax to the maximum allowable flow rate. As for the issue of the temperature being above 120C when flow rate is zero, that seems quite possible since collectors can reach very high "stagnation" temperatures when there is no flow through them. It may be that under those circumstances, your controller cannot meet 120C at any flow rate so hits its limit on the number of times that it can change control decisions before it "sticks" (oscillation limit parameter). Kind regards, David On 1/16/2011 16:49, Rambod Rayegan wrote:
-- *************************** David BRADLEY Principal Thermal Energy Systems Specialists, LLC 22 North Carroll Street - suite 370 Madison, WI 53703 USA P:+1.608.274.2577 F:+1.608.278.1475 d.bradley@tess-inc.com http://www.tess-inc.com http://www.trnsys.com |