Dear Héloïse, If you want to use the
ideal heating and cooling option of type56, you can change the set point at
wich you want to heat or cool. e.g. if you want to start
heating at T_op=T_set=20°C, determine an input to type56 being T_corrected =
2*Tset-Tmsurf, with Tset = 20 and Tmsurf the mean surface temp which type56
gives as an output. It comes from T_operative
= (T_air+T_mean_surf)/2, or with the symbols of above T_set =
(T_corrected+Tmsurf)/2. So, instead of supplying
the required operative temperature T_set as input, you supply the equivalent
air temperature, so with T_corrected as air temp and Tmsurf as surface temp you
end up with an operative temp = T_set. Works fine, with no
numerical issues, only a small oscillation around T_set, but with a small
enough time step, this is neglectable. Good luck, Maarten -- From: David BRADLEY
[mailto:d.bradley@tess-inc.com] Heloise, Dear TRNSYS users, The Type 56 uses a control on the
air temperature « TAIR » to compute the sensible heat demand of each
thermal zones. This temperature does not include
the surface temperature and doesn’t fully describe the temperature
actually felt by the human, body. Is there a way to control the
operative temperature, rather than on the air temperature, in type 56 ? I thought about using Type 22 but the
simulation seems rather unstable with more than on Type 22, and I would like to
be able to control the operative temperature in each thermal zones. Thanks for your help ! Best regards, Héloïse Pelen ETAMINE
Visitez notre site web : www.etamine.coop !
_______________________________________________ TRNSYS-users mailing list TRNSYS-users@cae.wisc.edu https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users
-- *************************** David BRADLEY Principal Thermal Energy Systems Specialists, LLC 22 North Carroll Street - suite 370 Madison, WI 53703 USA
P:+1.608.274.2577 F:+1.608.278.1475 d.bradley@tess-inc.com
http://www.tess-inc.com http://www.trnsys.com |