Welcome to the TRNSYS Users Forum.

The forum is a place where people can interact and have discussions about different topics involving the use of the TRNSYS software package. Here you can post topics for discussion or questions on using TRNSYS and get advice from other users or TRNSYS experts. This forum is not intended for detailed technical support. Users should contact their distributor’s hotline for such assistance.

Some tips for success on using the forum:

  • Follow the Forum Rules posted in Forum Administration.
  • There are categories for different types of topics and questions. Post your topic or question into the proper category.
  • Before posting a topic or question search the existing topics  (and the TRNSYS Users listserv archive or Post archive) to see if a similar topic or question has already been answered.
  • Use a descriptive topic name. Don’t use attention getting subjects, they don’t get attention and only annoy people.
  • State the version of TRNSYS and which add-ons your are using.
  • Include enough specific details for your topic of question to be answered. Just posting “Why am I getting an error?” without describing the specific error and what you are trying to do when you get the error will not receive a response that fixes your issue.
  • Remember when people help you, they are doing you a favor. Be patient, help people out by posting good descriptions of what you need help with, and be polite even if a response does not solve your issue.
  • Moderators may edit your post for clarity or move your topic to a more appropriate category.

Notifications
Clear all

TRNFlow and Type 56 Outputs

0 Posts
1 Users
0 Reactions
241 Views
0
Topic starter

Dear users, 
Just recently a question came up regarding the outputs of Type 56 and TRNFlow, that we would like to share here for clarification: 

Question:
I would like to ask a question about output variables when TRNFlow is enabled. When TRNFlow is used, Type56 reports the following outputs:

  • QVENT
  • QINF

Could you please briefly explain:

- the concept used to define QVENT and QINF when TRNFlow is enabled, and

- which airflow rates are used as the basis for the calculation and classification of QVENT and QINF.

Answer:
TRNFlow has three categories of "input mass flow rates" of airnodes (see TRNFlow manual Section 3.7. TRNFLOW Outputs; similar to Type 56 itself):

NTYPE 201: FLINZ Outdoor air infiltration flow per airnode [kg/h] from an external node (outdoor) into airnode:

  • is used to calculate NTYPE 4: QINF = air mass flow  * cp_air * (Tamb - Tairnode))

NTYPE 203: FLVSZ Ventilation supply flow per airnode [kg/h] Sum of all flows from auxiliary nodes into airnode

  • the disaggreated mass flow rate of NTYPE 203 and the related temperature differences are used to calculate NTYPE 5: QVENT

NTYPE 205: FLIZZ flow into thermal airnode from specified thermal airnode [kg/h] Sum of all flows from another specified airnode into the thermal airnode

  • inflow into a thermal airnode from a specified thermal airnode (coupling)


Question:
FLINZ, FLVSZ, and FLIZZ are not mapped directly to the Link type itself (e.g., Crack/Fan/Duct), but are determined by the types of nodes connected, i.e., where the flow comes from and where it goes.

Therefore, if a fan is connected directly from an external node to an airnode, the flow should be counted as FLINZ and thus contribute to QINF, not FLVSZ/QVENT.
On the other hand, if outdoor air is first taken into an auxiliary node (duct system) and then supplied to an airnode, it is counted as FLVSZ, and the outdoor air fraction of that supply is also reflected in FLTOZ.
Correct?

Answer:
Yes, that is correct.