[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] TRNSYS ground floor



Hi Dr. Tachon,

 

The U-Wert means how your wall transfer the heat and it’s normal that you get this change because you changed the thickness of your materials as well as his type (U-wert= Thermal conductivity/thickness). You may also consider your ground-on-slab as boundary wall by setting  to the inside (front) and outside (back) convective heat transfer coefficients. You can refer to volume, page 143 of the documentation

 

WALLS WITH KNOWN BOUNDARY CONDITION

 

A wall having a known boundary condition might be a concrete floor resting on ground of a known temperature or a wall adjacent to a zone whose temperature is known. The front of the wall is considered to be at the inside of the zone. Normally, the boundary condition is the temperature of a node connected to the back surface of the wall through a pure resistance. It is possible to specify the surface temperature of the outside by setting the back side heat transfer coefficient of the WALL Type (HBACK) to a very small value (less than 0.001 kJ/h/m²). This WALL Type is then only appropriate for use as a wall with a known boundary. The use of a very small value may be confusing but was kept for backwards compatibility reasons”

 

I Hope that’s helps

Hassan

 

 

Dr. Hassan Mahach

wissenschaftlicher Mitarbeiter

Arbeitsfeld Technische Innovationen

 

+49 681 844 972 23

mahach@izes.de

www.izes.de

 

 

IZES gGmbH | Altenkesseler Straße 17, Geb. A1 | 66115 Saarbrücken

Büro Berlin | Albrechtstraße 22 | 10117 Berlin

Telefon: +49 681 844 972 0 | Fax: +49 681 761 799 9

 

Rechtsform: gGmbH | Registergericht Saarbrücken HRB 8499

Steuernummer: 040 140 241 53 | USt.-IdNr.: DE 138 113 796

Aufsichtsratsvorsitz: Minister Jürgen Barke

 

Geschäftsführung: Prof. Frank Baur | Dr. Lesya Matiyuk

cid:image001.jpg@01D8905B.2921E320

 

Von: TRNSYS-users [mailto:trnsys-users-bounces@lists.onebuilding.org] Im Auftrag von Loic Tachon via TRNSYS-users
Gesendet: Dienstag, 5. Juli 2022 09:38
An: TRNSYS users mailing list at OneBuilding.org <trnsys-users@lists.onebuilding.org>
Cc: Loic Tachon <dr.loic.tachon@gmail.com>
Betreff: [TRNSYS-users] TRNSYS ground floor

 

Dear users,

 

I want to simulate a huge building (5500 m2) with a 20 cm concrete ground without isolation. 

I don't really understand how the direct contact boundary condition works.

 

I made a ground wall composed of 20 cm of concret and 80 cm of calcar.

 

I realize that the simulation result (Tzone temperature) is very dependent of the ground temperature boundary condition. 

I use type 77 with the depth of ground temperature of 1m, the amplitude of 12 and the mean temperature of 12.

If I change the parameters of type 77, the zone temperature results change a lots.

 

In the inf file, i get u value result of my floor : THERMAL CONDUCTANCE, U=     4.21086 kJ/h m2K; U-Wert=     0.97567 W/m2K

 

If I don't put the 80 cm of calcar, I get the following u value :

THERMAL CONDUCTANCE, U=    37.80000 kJ/h m2K; U-Wert=     3.77020 W/m2K

 

Is this normal ? What means U-Wert ?

 

 


 

--

Dr. Loïc Tachon 

(+33) 6 7440-0536 (France)