[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] Air-Water Heat Pump (Type 941) doesn't converge




Hello Jeff,

thanks very much for your answer. Maybe I didn't explain myself very well.

The waterflow of the heat pump is zero because the pump which controls the flow is turned off. The control signals of the heat pump (heating and cooling control signals) are zero too, so the heat pump should be turned off and nothing should happen. The problem is, the outlet temperature of the heat pump is unstable. I think the reason is that the heat pump is not completely turned off and is trying to solve this equation:

image.png

Obviously the equation can't be solved because m_dot_liq is zero, but the heat pump shouldn't be trying to solve it either.

As I said before, the documentation says something about a "Fan Control Signal" which should be set to zero, in order that the heat pump doesn't make any calculations. The problem is, I can't find that input when I look for it in the Simulation Studio.

I hope that I managed to explain myself well (English is not my native language). I would be very grateful if you can tell me if I'm wrong or what should I do.

Thanks very much,

Adrian Riebel






Libre de virus. www.avast.com

El mar., 7 jul. 2020 a las 13:40, Jeff Thornton via TRNSYS-users (<trnsys-users@lists.onebuilding.org>) escribió:

Adrian,

Any flow convergence issues you are having is likely due to something beyond the AWHP.  This type does not set the water flow rate - it simply passes it through the device; heating or cooling it of the device is on or simply just passing it through if the device is off.  Pumps are the devices in TRNSYS that typically set the flow rates for your loops.  I would suggest you use the TRACE feature and watch to see what is happening when you are getting convergence issues.

 

Jeff

 

---
Jeff Thornton President - TESS LLC 3 N. Pinckney Street, Suite 202, Madison WI USA 53703 Office: (608) 274-2577 Fax: (608) 278-1475 www.tess-inc.com E-Mail: thornton@tess-inc.com

On 07/05/2020 7:36 pm, Adrian Riebel Brummer via TRNSYS-users wrote:

Dear TRNSYS users,
 
I have a problem with Type 941 (Air-Water Heat Pump). My problem is that the simulation doesn't converge when the waterflow in the heat pump is zero, despite the heat pump is also in off mode (heating and cooling control signals are both set to zero).
 
I have read the mathematical reference of this Type and it says something about a "Fan control signal", which functions, as I understand, as the master on-off switch of the heat pump. The problem is that I can't find that Input in the TRNSYS programm.
 
I would like to know why I can't find that Input, and why the model doesn't converge despite the heat pump shouldn't be doing anything.
 
I send you a picture of all the inputs that I can see for this Type. I have TRNSYS18 and TessLibs17.
 
Regards,
 
Adrian Riebel
 
image.png

Libre de virus. www.avast.com

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org