[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] Type 123 Cooling Coil Psychometrics Problem



Daniel,

Type123 does a computation to find the maximum possible heat transfer at the given rated conditions (air and water inlet temperature, air inlet humidity, air and water flow rates). It then compares the stated capacity to the calculated maximum. In the case of the parameters that you have specified below, the maximum possible heat transfer is being calculated as 234. kJ/h. However! if you reduce the total and sensible heat transfer rates to that value you will run into another error.

Fundamentally, the problem is that while Type123 assumes that the coil is either totally dry or totally wet during operation its basic UA calculation method is invalid if the coil's rated conditions are for sensible-only heat transfer. We will certainly work on making some better error handling for Type123. I think the workaround for your case would be one of two things. You can either give the model some rated conditions in which the total capacity is greater than the sensible capacity or you could simply use a sensible-only heat exchanger model for your cooling coil.

kind regards,

 David


On 07/16/2019 06:19, Hofmann, Daniel via TRNSYS-users wrote:

Hello everyone,

 

I currently try to use Type 123 Cooling Coil with TRNSYS18. Type 123 is directly connected to the TRY2017 weather data reader. All other inputs to Type 123 are considered to be constant.

The rated parameter values are measured values and do not include any dehumidification.

 

 

No matter whether I use humidity mode 1 or 2 and no matter whether I reduce the total cooling capacity to e.g. 400 kJ/hr I always get the following error: “The referenced Unit has a bad parameter value. Reported information: Parameter #7, Reported Problem: The total cooling capacity of the coil is impossible at the given conditions.”

And an additional warning message is shown: “The referenced Unit has called the PSYCHOMETRICS routine one or more times during the simulation with a humidity ratio above the saturation humidity ratio for the given dry bulb temperature. The air was assumed saturated at the given dry bulb temperature and the humidity ratio set for this condition.”

 

I already checked the connection between the weather data reader and Type 123. I also tried a simulation with constant input values…..there is still not difference.

Thus I think it is a bug in Type 123 or the psych subroutine.

 

Does anyone have a solution or an idea what could cause the errors? Thanks a lot for any help!

 

Best regards

 

Daniel Hofmann

 


_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley@tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com