Noortje,
There is another alternative as well, which
is Type1267. It is a finite difference model that we wrote to
really dig into the coupling between buildings and the
surrounding ground. It is somewhat tricky to set up and it runs
slowly, however, it can model almost any configuration you want.
You can set up basements, partial basements (ie where the ground
slopes), etc. You can also embed pipes in the soil or in the
slab. Essentially what you are doing in this case is taking the
floor model out of Type56 and using this finite difference
approach which does not rely on transfer functions and does not
have a time base. The one thing that might be tricky for it is
to deal with a situation where you've got a radiant slab
between two floors in the building (as opposed to in a floor
that has some combination of insulation and soil on the back
side of it).
David
On 09/11/2018 09:33, Noortje Alders
wrote:
Dear David,
Thank you for your answer. This is
actually what I expected but hoped not to be the case. I think
the energy consumption of the building can be calculated
reliably; however, I would like to study the behaviour of the
floor heating in more detail. I guess I have to decide from
situation to situation which time-base to use, as the higher
the time-constant (the slower the system), the less the
time-base matters.
Op 11-09-2018 om 16:02 schreef David
BRADLEY:
Noortje,
The time base has to do with how often
the wall transfer functions are updated. The time base is
distinct from the simulation time step and while it is ideal
to have the time base and the time step be equal, it is
rarely possible. Ventilation and occupancy changes occur as
a function of the simulation time step. You'll see some
stepwise behavior in the room air temperature if your time
step and time base are different but in my experience this
does not lead to significant problems in computing either
the comfort or the energy consumption of the building. I
often have situations in which I use a 1-5 minute time step
and have to use a 1 hour wall time base in the building.
kind regards,
David
On 09/11/2018 03:12, Noortje Alders
via TRNSYS-users wrote:
Dear TRNSYS users,
I want to analyze the thermal
behaviour of a dwelling with floor heating in detail.
Attatched is a drawing of the floor construction. The
time-base is set by 1 hour by default. I would like to set
this time-base to a lower value (eg 15 minutes or less) to
be able to analyse the reaction to change in occupancy
with accordingly changing ventilation, heating setpoint
and internal gain. However, the high thermla mass and high
insulation value doesn't allow me to because the stability
criteria are not fullfilled. ("Error creating the wall
transfer coefficients: Stability criteria not
fullfilled"). In a previous thread of the forum (
http://lists.onebuilding.org/pipermail/trnsys-users-onebuilding.org/2012-November/024387.html
) I read that there is a "trick" for this. You can
devide one layer in the ground floor (e.g. the concrete
slab) with an active layer. However, if I try I get the
message that only one active layer is allowed. Is there
another way to tackle this problem?
Kind regards,
Klik hier om u aan te melden op
de Peutz Actueel
Klik hier voor het
cursusoverzicht van Peutz Academy
E-MAIL DISCLAIMER: http://www.peutz.nl/disclaimer/emaildisclaimer.html
_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org
http://lists.onebuilding.org/listinfo.cgi/trnsys-users-onebuilding.org
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley@tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
Klik hier om u aan te melden op de
Peutz Actueel
Klik hier voor het cursusoverzicht
van Peutz Academy
E-MAIL DISCLAIMER: http://www.peutz.nl/disclaimer/emaildisclaimer.html
--
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
3 North Pinckney Street - suite 202
Madison, WI 53703 USA
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley@tess-inc.com
http://www.tess-inc.com
http://www.trnsys.com
|