Niket, Your attachment does not seem to have come through with your email. If you want to see the building's response ONLY to the ambient temperature then you'll need to open the building file (*.b17) in TRNBuild and change the radiation calculation method from "internal" to "external by another component." To do so, navigate in TRNBuild to the "project" window and you'll see a list of "orientations." Click on each orientation and change from internal to external. Once you have saved the *.b17 file, return to the Studio, right click on the Type56 and select "update building variable list" from the context menu. Now when you open the building inputs, you'll see that there are three new inputs for each orientation (total solar, beam solar, and angle of incidence). Remember that any input whose value is not connected will remain constant at the given initial value. Set the initial value of all solar radiation inputs (as well as that of solar zenith and azimuth angles) to zero but leave the dry bulb temperature connection from Type15 to Type56 and your building will be subject only to an ambient temperature. kind regards, David
On 01/06/2017 05:18, Niket Kumar via
TRNSYS-users wrote:
-- *************************** David BRADLEY Principal Thermal Energy Systems Specialists, LLC 22 North Carroll Street - suite 370 Madison, WI 53703 USA P:+1.608.274.2577 F:+1.608.278.1475 d.bradley@tess-inc.com http://www.tess-inc.com http://www.trnsys.com |