Filippo and Jean, My approach to autosizing has been to run the building model in energy rate control with no setups or setbacks in the thermostat and to records the maximum hourly value of the QSENS NTYPE from Type56. This gives you the peak hourly sensible heating and cooling load for each zone in the building and is very similar to the autosizing that other programs do. You can then change the building back to a temperature level control simulation and use the peak heating and cooling loads to choose equipment. Be careful that you're sizing the cooling equipment based on a sensible demand not based on total cooling demand. kind regards, David On 09/03/2015 09:21, Jean Marais wrote:
-- *************************** David BRADLEY Principal Thermal Energy Systems Specialists, LLC 22 North Carroll Street - suite 370 Madison, WI 53703 USA P:+1.608.274.2577 F:+1.608.278.1475 d.bradley@tess-inc.com http://www.tess-inc.com http://www.trnsys.com |