[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] PID controller parameters setting



I recommend that you first consider using a different Type of cooling coil that does internal flow control calculations (such as Type508c).

PID controllers are useful in real machines, where things may change every millisecond. In simulations with reasonable timesteps of 1 minute or longer, PI controllers, or even just proportional controllers should be enough.

There is also an iterative controller (Type 22), which will slow the model down, but is capable of controlling as you would expect a real PID to behave.

I have also had some luck in TRNSYS using simple feed-forward type controls, where you predict the output using a simple equation then adjust that output with a proportional controller. For example:
control signal = predicted signal f(input 1, input 2) + adjustment f(actual result - desired result)

Ben Heymer. PE

On Tue, Sep 23, 2014 at 10:01 PM, 何磊 <swjtuhl822@126.com> wrote:
Hi everyone,
I have encountered some problems when the PID controller(type23) was used for controling the outlet air temperature of cooling coil.

The fluid flow rate of cooling coil is conected with a outlet of flow diverter(type11), the fluid flow rate of cooling coil is determined by the control signal of the flow diverter. It is in order to model a cooling cooling with a bypass in fluid side.

Then, the PID control is used for keeping the outlet air temperature (Controlled variable) of cooling coil at a setpoint, the control signal is the fluid proportion of the flow diverter. 

But no matter how to adjust the parameters of PID, the outlet air temperature oscillation cann't be eliminated.

so, I have two questions about this simulation.

1)How to determine the parameters of PID controller, sunch as Gain constant, Integral time and Derivative time, to avoid  Controlled variable oscillation ? 

2)is there some regular between the simulation time step and the parameters ? 

If anyone has experience in this respect, could please tell me how to choose the simulation time step and the PID parameters ?



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@lists.onebuilding.org