Dear Marcello, I just had a look into your model. There are actually two main reasons causing the deviation between your manual calculation and the TRNSYS Simulation.
1.
You haven’t set geosurf (beam radiation distribution factor) values, the shortwave radiation is then distributed area weighted to the surfaces, and consequently also to the windows. Therefore a part of the solar radiation leave
the zone depending on the transmissivity of the window. So if you set the geosurf value of the floor to one, all the short wave radiation will hit the floor.
2.
If you do so, there is still a large deviation because of the imperfect absorption of the radiation on
the floor. To solve this, set the absorption coefficients of the floor to 1 and apply a good insulation.
3.
There will be still a deviation of around 10 % caused by heat losses through the windows and walls. Best __________________________________________________________________________________________________ Jochen Lam TRNSYS Software Team
Curiestraße 2 70563 Stuttgart Fax: +49 711 67976-11 Web: www.trnsys.de
Von: TRNSYS-users [mailto:trnsys-users-bounces@lists.onebuilding.org]
Im Auftrag von marcello.caciolo@cofelyaxima-gdfsuez.com Dear TRNSYS users, I post again this message, hoping that someone can give a quick look to our sample project and give us some ideas on the reasons we don’t have the results we expected :
We have a little problem with type 56. I send you enclosed a sample project illustrating our problem. In type 56, we have one zone with 4 external glazed surfaces, with 4 orientations (namely ENE,
124 m2, SSE, 48m2, OSO,
124 m2 and Horizontal,
198 m2), and a boundary surface, with identical temperature. There are no internal loads. External radiation is fixed to
1000 kJ/hm2 on ENE,
2000 kJ/hm2 on SSE, 600 kJ/hm2 on OSO and
800 kJ/hm2 on horizontal, and assumed totally direct (ITotal = IBeam), with a zero incident angle for each orientation (this is no realistic, but we wanted to avoid problems with angle-dependant transmission coefficient). A cooling type is added to the building, in order to maintain ambient temperature to 26°C. All the windows have a SHGC of
0.387, for 0° incident radiation, calculated by LBNL Window, and a ratio of frame of 10 %. We expected cooling load, for static conditions, to be in the order of the result of following equation : (
IT_ENE*124
+ IT_SSE*48
+ IT_OSO*124
+ RadTotHor*198 )*
0.387 *
0.9 ! 124 = WinSurf ENE, 48 = WinSurf SSE, 124 = WinSurf OSO, 198 = WinSurf Hor ! 0.387 = Win SHGC ! 0.9 = 1-ratioFrame (TotalRad equation) However, TRNSYS give us almost half of this load (P froid in this picture, VS AppSolaires calculated by TotalRad equation). Do you have any idea of the reason our hand calculation is so far from TRNSYS calculation? Thank you for your help ! Best regards, Marcello Caciolo
P