Dear TRNSYS users, I am currently modeling a building with Thermo-activated building systems (TABS). As a first step, I try to compare TRNSYS results with stationary calculations provided by TABS manufacturer. A first simulation shows very different results. After few investigation, the main difference between TRNSYS and manufacturer calculation is due to convection heat transfer coefficients. Indeed, I activated in Type 56 automatic calculation for hconv for TABS surfaces. Temperature differences are very low, in the order of 1-2 degrees. In this case, the correlation: Hconv = alpha * DT ^0.31 Gives convection coefficients in the order of 5-10 (kJ/h)/(m2K) , even lower or much lower than standard coefficient for isothermal surfaces (11 (kJ/h)/(m2K) ). On the other hand, manufacturer data show convection coefficients in the order of 20-40 (kJ/h)/(m2K). My question is double: 1) Which is the origin of the standard coefficients (constants: 7.2 and 3.888, exponent: 0.31) used in the automatic calculation of hconv? 2) Do you have any experience in TABS? If yes, which value/correlation of hconv seems reasonable to you for these systems? Thank you for your attention. Best regards, Marcello Caciolo
P Pensez à l'environnement avant d'imprimer ce message |