Dear Talib, The method of adding data to extend the range of the performance file is correct. However, you need to also extend the actual performance data as well. For example, the provided data file shows a normalized capacity of 1.0469 and a fraction of design energy input of 0.98 for the following inlet conditions: Fraction of Design Load: 1.0 Chilled Water Setpoint: 10.0 C Entering Cooling Water Temperature: 32.2 C Inlet Hot Water Temperature: 116.11 C simply changing the inlet hot water temperature range so that the top value is 95C would result in the same performance (normalized capacity of 1.0469 and a fraction of design energy input of 0.98) for a different set of inlet conditions. More likely, the performance of the chiller would be quite different at such a low inlet hot water temperature. Some chillers may simply not be able to operate at lower inlet hot water temperatures. Best, David On 11/14/2012 07:16, Talib Ahmadu
wrote:
-- *************************** David BRADLEY Principal Thermal Energy Systems Specialists, LLC 22 North Carroll Street - suite 370 Madison, WI 53703 USA P:+1.608.274.2577 F:+1.608.278.1475 d.bradley@tess-inc.com http://www.tess-inc.com http://www.trnsys.com |