Re: [TRNSYS-users] Temperature and %RH setpoint TRNBUILD



David,
Thanks for your reply. From your equation, it seem that during period of 0 occupancy, I would get a temperature of 12 degree. But I would like the cooling to be switched off when there is no occupancy. So how should I go about defining the equation?

Thanks
Gary.

On Sep 19, 2012 4:00 AM, "David BRADLEY" <d.bradley@tess-inc.com> wrote:
Gary,
  Defining your setpoint as a SCHEDULE in TRNBuild simply allows you to set a value that depends upon the time of day. Defining your setpoint using an INPUT allows you a good bit more flexibility. You could define your equation as follows:

Tset_heat = 24*occ + 12*(1-occ)

occ would have to be defined in another equation or perhaps a Type14 forcing function to have a value of 1 when the building is occupied and a 0 when it is not occupied.

Best,
 David
  


On 9/17/2012 10:29, KUM GARY wrote:
Hi,

I trying to calculate the cooling demand of my office building in TRNBUILD and would like the cooling demand to response according to my occupancy schedule(less cooling at night and more cooling at day). I try to define the set temp at the cooling type by i not sure which one should i use (schedule or input?) And also the equation behind it, because when i enter like for instance 24degree(set temp) *occupancy schedule+0, i would get 0 degree when there is no occupancy.

Appreciate your kind assistance on this

Gary Kum


_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
d.bradley@tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com