Re: [TRNSYS-users] question on TYPE 676 (Steam-Fired Double-Effect Absorption Chiller)



This is the exact method employed by a major absorption chiller manufacturer to characterize the performance of their machines over a wide range of operating conditions.

Jeff

---
Jeff Thornton
President - TESS LLC
22 N. Carroll Street, Madison WI USA 53703
Office: (608) 274-2577  Fax: (608) 278-1475
www.tess-inc.com
E-Mail: thornton@tess-inc.com


On 06/14/2012 1:47 am, Lei Wang wrote:
Dear All,

I have a question on Type 676. According to the help documents,  the
energy delivered to the chiller by the steam source is calculated
using equation 676.4
Qsteam=(Capacity_rated/COP_rated)*F_designEnergyInput.

The F_designEnergyInput is the value returned by the thrid call to
Dynamic Data and is the value specified in the S3 data file. It only
is the function of cooling water temperature and the fraction of
design load, which is calcuated by equation 676.3 .
f_DesignLoad=Q_remove/Capacity_rated


 The energy consumption calculation is only based on the fraction of
design load, cooling water temperature and don't consider chilled
water outlet temperature. The chilled outlet temperature is only used
for calculating Capacity (specified in the S2 file).

 In my opinion, I don't think this model can calculate the energy
consumption correctly, when the chilled water supply temperature is
reset.

Thanks

Lei Wang