[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] weird Qcool



Dear Wang,

You are right : the Tcool I gave you was equal to 26, not to 24°C. Tset value is not important as well, the most important is that you understand how to do to define Tset.
In your model, your heating and cooling advices seem to work fine. Your problem comes frome your internal gain : 31 people are defined all the time in a room of approximatively 80 m², without schedule.
Because of your important internal gains, air temperature increases until 35°C in winter. Then air temperature is refreshed because Tcool = 35°C in winter.
In summer, air is cooled at 24°C, because this is the temperature you define in your cooling advice.

Best regards

www.itf.biz
www.itf.biz
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
ITF
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel@itf.biz ou aj@itf.biz
Afin de contribuer au respect de l'environnement, merci de n'imprimer cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email

Le 12/06/2012 18:19, 王洋 a écrit :
Dear Adrien Jezequel,

Thanks for your quick reply!
Tcool = 35 - 9 * Summer means if in summer, Tcool = 26 °C?

I tried
to run the simulation based on your solution Tcool = 35 - 9 * Summer, the result is also like the last Attached.
Oppositely,
it is not my heating system seems to work all the time, it is my cooling system seems to work all the time.
I set internal gains all the year.

Please see the Attached *.tpf and *.bui files, if you have free time , please help me have a look and give me some solutions.

Many thanks in advance!

Br.

wang



2012/6/12 ITF - Adrien JEZEQUEL <a.jezequel@itf.biz>
Or sorry, I made a mistake in my previous mail :
  • Tcool = 35 - 9 * Summer (instead of 35*winter  - 9*summer)
Regarding your heating system it may be something like :
  • Theat = 21*Winter
Regarding your attached picture, your heating system seems to work all the time.
In summer, either you cool at 21°C, either there is no internal gains defined, and you heat at 21°C.
Check your differents inputs.
You can procede step by step (internal gain = 0, ventilation = 0, infiltration rate = 0...) to see the influence of each parameters in your model to catch your issue.

Best regards

www.itf.biz
www.itf.biz
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
ITF
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel@itf.biz ou aj@itf.biz
Afin de contribuer au respect de l'environnement, merci de n'imprimer cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email

Le 12/06/2012 17:47, 王洋 a écrit :
Dear Adrien Jezequel,

Many thanks!

I think you'd better put for cooling temperatures

  • 35°C in winter (no cool) - heating temperature at 21°C
  • 24°C in summer
which may be translated in an equation tool by something like :
  • summer = GE(TIME,2162)*LT(TIME,6552)
  • winter = 1 - summer
  • Tcool = 35*Winter - 9*Summer
For Tcool = 35*Winter - 9*Summer, do you mean if in winter, Tcool = 35 °C, so Cooling doesn't work ; if in summer, Tcool = -9°C or 24 °C?

Meanwhile, another weird phenomena appear: After running based on your solution in winter, indoor temperature becomes 35 °C also not 21 °C, although I set heating temperature as 21 °C; in summer, however, indoor temperature becomes 21 °C. Please see the Attached On-Line Plotter image.
Furthermore, when I create another Tcool equation as 35*winter+24*summer, the result is also like the Attached On-Line Plotter image.

Please give me some solutions or advices!
I think the point how to set that Cooling doesn't work in winter? The possible reason of that problem is that I also set a Mechanical Ventilation in winter (Tset=19 °C) and summer
(Tset=17 °C). I guess Maybe the Mechanical Ventilation will influence on Cooling and heating?

Many thanks in advance!

Br.

wang 



2012/6/12 <trnsys-users-request@cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
       trnsys-users@cae.wisc.edu

To subscribe or unsubscribe via the World Wide Web, visit
       https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
       trnsys-users-request@cae.wisc.edu

You can reach the person managing the list at
       trnsys-users-owner@cae.wisc.edu

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."

Today's Topics:

  1. Re: TRNSYS-users Digest, Vol 90, Issue 23
     (jose.gonzalez@imdea.org)
  2. Re: weird Qcool (ITF - Adrien JEZEQUEL)
  3. Flue gas stack in TRNSYS (Mazen Darwish)
  4. AutoReply: TRNSYS-users Digest, Vol 90, Issue 23
     (kelelo1@kelelo.com)


---------- 已转发邮件 ----------
From: <jose.gonzalez@imdea.org>
To: trnsys-users@cae.wisc.edu
Cc: 
Date: Tue, 12 Jun 2012 14:56:21 +0200 (CEST)
Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 23
I am out of the office from Monday, June 11 to Friday, June 15 and unable to respond at this time.

For any urgent matters, please contact Dr. Manuel Romero (manuel.romero_at_imdea.org).

Thank you for your understanding.

Best regards,

José Gonzalez-Aguilar



---------- 已转发邮件 ----------
From: ITF - Adrien JEZEQUEL <a.jezequel@itf.biz>
To: trnsys-users@cae.wisc.edu
Cc: 
Date: Tue, 12 Jun 2012 15:26:28 +0200
Subject: Re: [TRNSYS-users] weird Qcool
Dear Wang,

As far as I understand, the cooling set temperature you define in your model is :
  • 24°C in summer, which seems to be correct
  • and 0°C in winter... which seems to be wrong, since you don't refresh your thermal zone at 0°C in winter!
That's why you obtain huge cooling loads.
BAL_ENERGY is not 0 because you heat and cool in the same time in winter.

I think you'd better put for cooling temperatures

  • 35°C in winter (no cool) - heating temperature at 21°C
  • 24°C in summer
which may be translated in an equation tool by something like :
  • summer = GE(TIME,2162)*LT(TIME,6552)
  • winter = 1 - summer
  • Tcool = 35*Winter - 9*Summer

Best regards


www.itf.biz
www.itf.biz
Adrien JEZEQUEL
Simulations Thermiques Dynamiques
ITF
62, Rue du Bolliet
73230 St Alban Leysse
FRANCE
Phone :
Fax :
Mail:
+33(0) 479 750 029
+33(0) 479 852 122
a.jezequel@itf.biz ou aj@itf.biz
Afin de contribuer au respect de l'environnement, merci de n'imprimer cet e-mail que si nécessaire
Please, consider our environmental responsability before printing this email

Le 12/06/2012 14:55, 王洋 a écrit :
Dear all,

I make a simulation. The cooling set temperature is 24*Summer schedule (2162 h to 6552 h), The heating set temperature is 21*Winter schedule (the rest hours). After running, however, it appears WEIRD phenomenon. Please see the ATTACHED Energy_zone.BAL file. During the winter period, there are Qcools and Qcool is very large up to 47000 kJ. And then it results in wrong BAL_ENERG, it is not 0.

Please give me some advices and solutions to that!

Many thanks in advance!

Br.

wang 


2012/6/11 <trnsys-users-request@cae.wisc.edu>
Send TRNSYS-users mailing list submissions to
       trnsys-users@cae.wisc.edu

To subscribe or unsubscribe via the World Wide Web, visit
       https://mailman.cae.wisc.edu/listinfo/trnsys-users
or, via email, send a message with subject or body 'help' to
       trnsys-users-request@cae.wisc.edu

You can reach the person managing the list at
       trnsys-users-owner@cae.wisc.edu

When replying, please edit your Subject line so it is more specific
than "Re: Contents of TRNSYS-users digest..."

Today's Topics:

  1. Re: TRNSYS-users Digest, Vol 90, Issue 21
     (jose.gonzalez@imdea.org)
  2. AutoReply: TRNSYS-users Digest, Vol 90, Issue 21
     (kelelo1@kelelo.com)
  3. type666 (Andr?s Montero)
  4. Type 673 heating problem (Santeri Siren)


---------- 已转发邮件 ----------
From: <jose.gonzalez@imdea.org>
To: trnsys-users@cae.wisc.edu
Cc: 
Date: Mon, 11 Jun 2012 16:07:28 +0200 (CEST)
Subject: Re: [TRNSYS-users] TRNSYS-users Digest, Vol 90, Issue 21
I am out of the office from Monday, June 11 to Friday, June 15 and unable to respond at this time.

For any urgent matters, please contact Dr. Manuel Romero (manuel.romero_at_imdea.org).

Thank you for your understanding.

Best regards,

José Gonzalez-Aguilar



---------- 已转发邮件 ----------
From: kelelo1@kelelo.com
To: trnsys-users@cae.wisc.edu
Cc: 
Date: Mon, 11 Jun 2012 14:10:47 GMT
Subject: [TRNSYS-users] AutoReply: TRNSYS-users Digest, Vol 90, Issue 21

I will be out of the office from June 8 - 23 on a backpacking trip with my son and his Venture Crew at Philmont Scout Ranch in New Mexico. I will not have access to email or phone service while I am gone, but I will reply to your message as soon as possible after I return to the office on Monday, June 25th.

Thank you for your patience,
Mark Thornbloom




---------- 已转发邮件 ----------
From: "Andrés Montero" <andresmonteroi@gmail.com>
To: trnsys-users@cae.wisc.edu
Cc: 
Date: Mon, 11 Jun 2012 16:57:30 +0200
Subject: [TRNSYS-users] type666
Dear Trnsys users,

In order to simulate a water-cooled chiller, first I need to create the 2 external files for this component. 
I'm trying to find some catalogues with information of a 40 to 45 kW water-cooled chiller but the web pages I run into it, ask me to register, but I'm still waiting the username and pasword. Does anyone has a catalgoue with this type of info regarding this cooling capacity machine?

Best regards,

Andrés

--
Andrés Montero I.



---------- 已转发邮件 ----------
From: Santeri Siren <santeri.siren1@gmail.com>
To: "trnsys käyttäjät" <trnsys-users@cae.wisc.edu>
Cc: 
Date: Mon, 11 Jun 2012 19:56:40 +0300
Subject: [TRNSYS-users] Type 673 heating problem
Dear all,

I cant make type673 heating mode to work. Cooling mode works just fine but when I change the cooling control signal to 0 and heating control signal to 1 it doesnt work anymore. When the heating mode is used nothing happens. Does anyone know why?

Best regards,
Santeri Siren

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users




_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users


---------- 已转发邮件 ----------
From: Mazen Darwish <mazentd@gmail.com>
To: trnsys-users@cae.wisc.edu
Cc: 
Date: Tue, 12 Jun 2012 16:05:51 +0200
Subject: [TRNSYS-users] Flue gas stack in TRNSYS
Hello everyone ,
 
Is there a way to model a flue gas stack in TRNSYS , i need to recirculate hot air and flue gases from the economizer in an HRSG back to a solar tower .
 
i appreciate your ideas.
 
Mazen Darwish
KTH Royal Institute of Technology
Department of Energy Technology
Brinellvägen 68, SE-100 44 Stockholm, Sweden


---------- 已转发邮件 ----------
From: kelelo1@kelelo.com
To: trnsys-users@cae.wisc.edu
Cc: 
Date: Tue, 12 Jun 2012 14:23:03 GMT
Subject: [TRNSYS-users] AutoReply: TRNSYS-users Digest, Vol 90, Issue 23

I will be out of the office from June 8 - 23 on a backpacking trip with my son and his Venture Crew at Philmont Scout Ranch in New Mexico. I will not have access to email or phone service while I am gone, but I will reply to your message as soon as possible after I return to the office on Monday, June 25th.

Thank you for your patience,
Mark Thornbloom



_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users