[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] calculation of unmet hours



Hello Sir,

 

Thank you very much for quick reply.  I have a question about Power Coefficient of Pumps and Fan. This is a parameter which is required for calculation of power consumption of Pump and Fan. It is a user defined value. My question is : How can I calculate the power coefficient or there is some standard value for constant speed and variable speed pump and Fans? Please guide me. If there is some literature about it please specify.

 

Regards,

Mayank

 

From: David BRADLEY [mailto:d.bradley@tess-inc.com]
Sent: Thursday, March 22, 2012 10:34 PM
To: Mayank
Subject: Re: [TRNSYS-users] calculation of unmet hours

 

Mayank,
  If you have access to the TESS Utility Library, you can use the "zone temperature watcher: Type584." When zone temperature exceeds the setpoint, you have an "unmet hour." If you do not have Type584, you can write an equation that has a value of 1 if the zone temperature exceeds the setpoint temperature.

  On a related note, he first important thing to do is to define what you mean by "unmet hours." In the industry, most often people refer to "unmet load hours" If you are running your Type56 in energy rate control mode (where you define a setpoint temperature and HEATING and COOLING types inside TRNBuild and use the QSENS NTYPES to predict your sensible energy loads) then you have the choice as to whether you limit or do not limit the capacity of your idealized heating and cooling system. If you limit the heating or cooling capacity then an unmet load occurs whenever the Type56 zone temperature exceeds the cooling setpoint temperature or falls below the heating setpoint temperature.

  If your building is operating in temperature level control (where you define a thermostat, an actual HVAC system and the zone temperature reacts to what the HVAC system is doing) then "unmet load hours" are meaningless because the "load" is never calculated at the space level (the space reacts to the HVAC system's operation, it only indirectly commands the HVAC system). In this case, we typically redefine "unmet load" as time spent outside the throttling range of the thermostat (ie above or below the deadband). Again Type584 is used to total the amount of time.
Kind regards,
 David

On 3/19/2012 03:42, Mayank wrote:

Hello Everyone,

 

I need to calculate unmet hours of my system. Is there any component in TRNSYS 16 or I have to make manual calculation.

 

Please guide me.

 

Regards,

 

Mayank Bhatnagar

M.Tech.(Energy Engineering)

Malaviya National Institute of Technology,

Jaipur (INDIA)

Ph.: +91-9983816468

 




_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://mailman.cae.wisc.edu/listinfo/trnsys-users



-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA
 
P:+1.608.274.2577
F:+1.608.278.1475
d.bradley@tess-inc.com
 
http://www.tess-inc.com
http://www.trnsys.com