Zhou, I don't think you've done anything incorrect in your project. I think there are a few reasons for your low cooling load. 1. there is only one window in the building allowing solar heat gains into the space. 2. the internal gains (equipment, lighting) are very small (50W in the sun and back zones). This means that the building internal temperature isn't being driven up by much. 3. the floor slab is uninsulated and coupled directly to a constant 10C temperature all year round (this provides some free cooling). 4. all three zones have 0.5 airchanges per hour of infiltration (ambient air). While that is not unreasonable, infiltration typically increases heating loads and decreases cooling loads. I would also recommend raising the zone thermal capacitance values to 5 times their default. The default accounts only for the thermal capacitance of the air in the zone. It neglects the capacitance of the furnishings. I would also recommend setting the humidity capacitance multiplier to 10 instead of 1; a value of 1 indicates that only the air in the zone has any ability to absorb and desorb moisture. These will have secondary effects on your cooling load. Regards, David On 11/8/2010 06:56, jw_zhou wrote:
-- *************************** David BRADLEY Principal Thermal Energy Systems Specialists, LLC 22 North Carroll Street - suite 370 Madison, WI 53703 USA P:+1.608.274.2577 F:+1.608.278.1475 d.bradley@tess-inc.com http://www.tess-inc.com http://www.trnsys.com |