[Date Prev][Date Next][Thread Prev][Thread Next][Date Index][Thread Index]

Re: [TRNSYS-users] Problem with Type 55: Periodic Integrator - reset time



Eric,
 I think your parameter set has some overlapping intervals.

- parameter 5 determines when the input resets to zero (in your case, it is resetting daily at midnight)
- parameter 2 determines when in that 24 hour period the integrator starts paying attention (by setting it to 1, it is ignoring the fist hour in the 24 hour period)
- parameter 3 determines how long the input should be evaluated (by setting it to 24 and starting at 1, you're progressively evaluating one hour longer than your reset time each day of the simulation (1+24 = 25...)

try setting parameter 2 to 0 and see if that cures the problem. I'm not sure why it is behaving properly when you start a new project.
Best,
 David


On 7/20/2010 20:25, Eric Wilson wrote:
Hi all,

In a project of mine, none of my Type 55 integrators reset after a cycle as they should (they continue to integrate until the end of the simulation), unless they are set to a monthly cycle with a value of -1. In a blank new project, they work fine.  Has anyone encountered this problem?

* Model "Type55" (Type 55)
*

UNIT 78 TYPE 55     Type55
*$UNIT_NAME Type55
*$MODEL .\Utility\Integrators\Periodic Integrator\Type55.tmf
*$POSITION 815 50
*$LAYER Main #
PARAMETERS 7
1        ! 1 Integrate or sum input
1.0        ! 2 Relative starting hour for input
24        ! 3 Duration for input
24        ! 4 Cycle repeat time for input
24        ! 5 Reset time for input
start        ! 6 Absolute starting hour for input
stop        ! 7 Absolute stopping hour for input
INPUTS 1
supply_diam        ! HVAC_Inputs:supply_diam ->Input
*** INITIAL INPUT VALUES
0.

Many thanks,
Eric

--
Eric Wilson
M.S. Candidate, Building Systems Program
Dept of Civil, Env., and Arch. Engineering
University of Colorado at Boulder
_______________________________________________ TRNSYS-users mailing list TRNSYS-users@cae.wisc.edu https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users

-- 
***************************
David BRADLEY
Principal
Thermal Energy Systems Specialists, LLC
22 North Carroll Street - suite 370
Madison, WI  53703 USA

P:+1.608.274.2577
F:+1.608.278.1475
bradley@tess-inc.com

http://www.tess-inc.com
http://www.trnsys.com