Sebastian,
I would think that all you would need would be Type56 and Type109 (plus Type33 and Type69 I think). You can just set the cooling temperature in your zones to 24.2C and allow the cooling equipment to have unlimited power, then take a look at the maximum cooling load that was required. That should give you the required system size. Keep in mind three things:

1. Type109 reads a typical (average) weather year file - not an extreme one and typically (right or wrong) system sizing is done based on a worst-case scenario, not on an average year.

2. If you plan for your lab to have temperature setups and setbacks, your max cooling load will be enormous because technically the load is infinite when your set point temperature comes back from its set up condition. I would recommend using a constant setpoint in order to find your system size.

3. The Type56 output QSENS is sensible cooling only! In order to get a latent component, you must also impose an RH setpoint on the zone and look at the QLAT output from Type56. This isn't ideal because often the latent cooling is an effect of the sensible cooling (not something that can be controlled separately). We wrote a component based on some curve fits that calculate the amount of latent cooling that a "cooling coil type" of cooling device can do based on zone temperature and ambient wet bulb (If I am remembering correctly). Its latent cooling ability turns into a negative moisture gain on the space, which is fed back to Type56. The component will be part of the TESSLibs 3.0 but for the moment is an individual component.
Kind regards,
David


Sebastian Schlott wrote:
My Problem,

I have 2 rooms, used as a lab.

In this rooms there is a thermal load of 15kw which has to be cooled away.

The ambition is the simulation of the room temperature. Target: 24°C +- 0,2 °C
Question: Is the installed system strong enough, which systempower do I need?

At the moment the installed system has not the ability to cool 15 kw away.

is it enough to use the build (type56) and weather data(Type109) to simulate this situation?

Mit freundlichem Gruß

i. A. Sebastian Schlott


------------------------------------
Kuehn Bauer Partner
Beratende Ingenieure GmbH
Wilhelm-Wagenfeld-Strasse 6
80807 München

T: +49 89 189 16-182
F: +49 89 189 16-110
E: ses@kbp.de

Geschäftsführung: Michael Kuehn jr.
HRB 102024
------------------------------------

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@cae.wisc.edu
https://www-old.cae.wisc.edu/mailman/listinfo/trnsys-users




--
***********************************************************************
Thermal Energy System Specialists (TESS), LLC David BRADLEY 22 N. Carroll Street - Suite 370 Partner Madison, WI 53703 USA P: +1.608.274.2577 F: +1.608.278.1475 E-mail: bradley@tess-inc.com Web Pages: http://www.tess-inc.com and http://www.trnsys.com

***********************************************************************