Sotiris, If your absorption chiller is producing chilled water at a particular flow rate and is connected to a series of fan coils then the only way to increase the capacity of the fan coils is to modify their air-side flow rate and to put on a larger absorption chiller. Changing the size of the absorption chiller involves changing the external files that are referenced by Type107. As for convergence, if you are getting a warning saying that convergence could not be reached, that means that TRNSYS was unable to solve your system to within the specified tolerances at that time step. If you are getting a few such warnings throughout an annual simulation, it is not something to be concerned about. If you are getting a lot of those warnings then probably the system or the controls are not well enough defined. I would recommend that you read a few sections of the documentation to get a good understanding of how TRNSYS is trying to solve your system: Section 7.3.17 of the 07-TRNEdit manual "the SOLVER statement" Section 5.1 of the 05-Mathematical Reference manual (the first section under "controllers") Kind regards, David SOTIRIS KONSTANTELOS wrote:
-- *********************************************************************** Thermal Energy System Specialists (TESS), LLC David BRADLEY 22 N. Carroll Street - Suite 370 Partner Madison, WI 53703 USA P: +1.608.274.2577 F: +1.608.278.1475 E-mail: bradley@tess-inc.com Web Pages: http://www.tess-inc.com and http://www.trnsys.com *********************************************************************** |