Nguan, Two things occur to me. First, if you take the max of each zone and then sum them, you will probably get a higher value than if you had summed the cooling load of the zones, then taken the max. In the first case, if all of your zone's have their max cooling load at different times then you can get away with putting in a smaller cooling system because it will never have to serve all zones at the same time with their maximum requirement. Second, the QCOOL that you are getting from Type56 is sensible cooling only. It doesn't account for any latent cooling that might have to be done as well and therefore does not represent the total cooling. If you are doing latent cooling, you will need to activate the "dehumidification" in TRNBuild as well as cooling. Be a bit careful, however, dehumidification and cooling are treated completely separately from one another; you can have cooling without dehumidification and dehumidification without cooling. Kind regards, David #TEO NGUAN TECK# wrote:
-- *********************************************************************** Thermal Energy System Specialists (TESS), LLC David BRADLEY 22 N. Carroll Street - Suite 370 Partner Madison, WI 53703 USA P: +1.608.274.2577 F: +1.608.278.1475 E-mail: bradley@tess-inc.com Web Pages: http://www.tess-inc.com and http://www.trnsys.com *********************************************************************** |