[TRNSYS-users] Question concerning Type 107 (Single Effect Hot Water Fired Absorption Chiller)
Dear TRNSYS users,
I have problems setting up the input file required by type 107 from
manufacturers data.
To make this easier I would like to ask You to look up the following
example and correct it if necessary:
I have a chiller with
Rated capacity = 35kW
Rated Energy Input = 50,2kW
One exemplary operation point:
T_hot_in=70°C
T_medium_in=27°C
T_cold_setpoint=7°C
P_hot_in=20,3kW
P_cold_out=13,5kW
Calculated fraction of design load:
f_design_load=(m_cold*cp_cold*(T_cold_in-T_cold_setpoint)/Capacity_rated
=(1,53kg/s*4,20kWs/kgK*2,1K)/(35kW)
=0,386
Calculated fraction of full load capacity:
F_full_load_capacity=13,5kW/35kW=0,386
Calculated fraction of design energy input:
F_design_energy_input=20,3kW/50,2kW=0,404
The following numbers would form one row in the input file.
T_hot_in=70°C
T_medium_in=27°C
T_cold_setpoint=7°C
f_design_load=0,386
F_full_load_capacity=0,386
F_design_energy_input=0,404
I doubt that the "fraction of design load" and "fraction of full load
capacity" should be the same....
So what is the difference between the two. If the latter is the maximum
chilling capacity I could get from the machine (what I suppose right
now) how is it defined? As far as I know manufacturers do not deliver
that number...
Best regards,
Jochen
--
_________________________________________________
Dipl.-Ing. (FH) Jochen Döll
Dept. Thermal Systems and Buildings
Fraunhofer-Institut für Solare Energiesysteme ISE
Heidenhofstrasse 2, 79110 Freiburg, Germany
Phone: +49 (761) 4588-5456
Fax: +49 (761) 4588-9000
Mail: jochen.doell@ise.fraunhofer.de
Web: www.ise.fraunhofer.de
_________________________________________________