Re: [TRNSYS-users] Type 31 with high mass flows



Dear Jens:

From your message, I understand that you are trying to assess the sensitivity of the solution with respect to the discretization of the pipe. If you look at the Fortran code of TYPE31, you will see that it calculates the fraction FLOW*DELT / MASS, where FLOW is the mass flow rate entering the pipe, DELT the time step, and MASS the total mass that the pipe can contain (density*volume).

There are two limits for this fraction:
- If this ratio is very small (less than a tolerance TOL = 0.001), then the pipe is not updated and only the thermal losses are calculated. - if this fraction is greater than 1, you will get the error message 'flow is bigger than the capacity of the pipe during one time step'.

As the TYPE31 is not a regular finite differences method, but a plug model, you have to keep in mind these limits if you want to run a sensitivity analysis of the solution with respect to the pipe discretization. I would recommend looking at section 5.6.4 of the 05-MathematicalReference.pdf, where you will find an explanation of the plug model.

I hope this explanation helps.

Diego


does the Type 31 pipe have got any problems with
segments (mass flow times the timestep) that are
bigger than the pipe itself.?
I study heat losses of pipes that are through-flown by
different mass flows from a DHW load profile (always
the same).
I tested 1, 7 and 14 interconected pipes having all
the same total volume and length with different time
steps (60s, 20s, 6s). That leads to a variety of
maximum segment masses and I get differences in heat
losses of up to 7 per cent.
I know that TRNSYS 16 writes a warning when the mass
flow is bigger than the capacity of the pipe during
one timestep but I have no closed loop, just a type 6
and the pipe.

Jens Apel
FHTW Berlin, Germany

--

Diego A. Arias
TRNSYS Coordinator
Solar Energy Laboratory
University of Wisconsin - Madison