Dear Xavier,
Wind effects on buildings are quite complex, depending on building geometry, on wind speed, on wind direction, on penetrations through the building envelope (doors, windows, etc.) and on local terrain (trees, surrounding buildings, etc.). TRNSYS includes a number of methods for estimating these effects. If all you want is a very basic estimation of a wind speed dependent heat transfer coefficient, you can use the ASHRAE equation:

h = a1 + a2*V + a3*V^2

where a1, a2, and a3 are in W/K.m2 and depend on the exterior surface material. For stucco, a1 = 11.58, a2 = 5.894, and a3 = 0. For glass, a1 = 8.23, a2 = 3.33 and a3 = -0.036. (From ASHRAE Standard 140)

The next step up in complexity of predicting the effect of wind induced infiltration is to use one of ASHRAE's simplified methods: either the K1, K2, K3 approach, or the Sherman Grimsrud equation. There are components in the TESS Utility Library that will calculate infiltration using these methods.

The final level of complexity is to make use of standard TRNSYS Type157 (connection to COMIS) or Type97 (Connection to CONTAM). These components provided data links between TRNSYS and two different airflow modelling tools. There is some redundancy of data entry in that you have to describe the building thermal model in TRNBuild, then describe the building geometry in CONTAM or COMIS. Once defined, however, the programs work together to do combined thermal / airflow modeling of the building. COMIS is available as an add on to TRNSYS from CSTB. CONTAM is freely available for the US National Institute of Standards and Technologies (http://www.bfrl.nist.gov/IAQanalysis/CONTAMWdesc.htm). As a final alternative, you can use another TRNSYS add-on called TRNFLOW. TRNFLOW is an adaptation of COMIS. It is available from Transsolar and provides a combined front end for the specification of both the airflow and the thermal model inside TRNBuild.
Kind regards,
 David



Xavier Dequaire wrote:

Hi,

type 56 does not take wind  as an input,

Any method to simulate the effects of wind on the energy consumption of
the building?

thank you

Xavier D.

_______________________________________________
TRNSYS-users mailing list
TRNSYS-users@engr.wisc.edu
https://www.cae.wisc.edu/mailman/listinfo/trnsys-users

--
**
David BRADLEY
Solar Energy Laboratory
University of Wisconsin - Madison
1500 Engineering Drive
Madison, WI  53706
United States

Ph: +1 608 263 1589
Fax: +1 608 262 8464

Email: dbradley@engr.wisc.edu